03-12-2007, 01:45 AM
Hello guys,
I have to replace the refrigerant of 8 panasonic airco units to R417. My boss says I can just recover the R22, vacuum the system and put R417 on it. Is this true?
Do I have to use the same amount as if it is R22?
Thanks!
Eric.

Contactor
03-12-2007, 01:49 AM
Eric

Is R22 being phased out now in Belgium? We can still buy it here in the UK.

on4hf
03-12-2007, 02:01 AM
I've been told that the air conditionings running on R22 have to be replaced by other units (running on something else than R22) or the refrigerant changed by 2010.
If you encounter a unit with a leak and you have to fill it with more than 5% you are not allowed to do so. Instead of changing the unit I can change the refrigerant into R417. That's what the customer told me and my boss says also. I was just wondering if I need the same amount of refrigerant.
Eric.

REEFER-TEK
03-12-2007, 06:34 AM
Take a look at R407c as an alternative. It is as close to r-22 and is a HFC

Stuart
03-12-2007, 12:37 PM
Hey guys,:eek:

Just before you go and dump a charge of R407C in these units....Just remember that it is NOT compatable with mineral oil.

407C is a retrofit not a drop in.

Be careful otherwise you may just end up costing yourselves a lot of money to replace the units. Also when using R407C remember that a separate set of gauges should be used to avoid cross contamination.

Why not just fix the leak and recharge with R22?????:(

The new gas will be R410A which runs at a higher pressure, uses a different oil and requires a different grade of copper pipework.

All the best guys

l'robot
03-12-2007, 02:50 PM
If it is R417A(Isceon59) then you should use about 10% more charge than with R22. This is a straight drop in replacement for R22.
Do not use R407C!

Pol
03-12-2007, 05:26 PM
on4hf,

Yes you can use R417 (Isceon 59) on R22 installations. You do not need to change anything to the installation. We`ve had some sets running for quite some time now, no problems there at all.

you need different types of oil for R22 and R407c, so can`t do. R410, totally different pressures, can`t do either. R417 is prefect for replacing R22 without changing the oil.

I believe it`s pretty expensive, though.

Take care,

Pol

on4hf
03-12-2007, 06:51 PM
Thanks for the replies everybody.
I went to the customer today and changed the refrigerant on 5 of the 8 units. I have noticed that it needs a little more when filling with R417A, so I did put some extra.
Tomorrow I will take the other 3. Also from 2 units the compressor won't start. The current is 45A for a small unit. I think the compressors are dead, but that's another story...

Eric.

paulwild
16-12-2007, 01:18 PM
hello mate
we now as a matter of course change from r22 to r417 every time we encounter a unit with a leak or requires a major component change, we ave ad no probs after conversion , as previous posters have said you will require a slightley bigger charge
cheers paul

Makeit go Right
16-12-2007, 09:59 PM
we now as a matter of course change from r22 to r417 every time we encounter a unit with a leak or requires a major component change, we ave ad no probs after conversion. As previous posters have said you will require a slightley bigger charge
cheers paul

That is a very sensible policy.....come 2009 there is going to be a real frenzy with customers finally realising that there will be no more new R22 for topping up - just the salvaged stuff for a short while. Any customers that can get their systems converted to R417a / MO59 before then should do that. (Possibly as part of a maintenance visit?)