In Aqua-Ammonia absorption refrigeration, what factors determine the rate of absorption of the ammonia gas into the return fliud flowing down the absorber coil / vessel ???? . Can the Aqua-ammonia solution become saturated with ammonia, such that it can't absorb any more ammonia ???

Pooh
12-11-2007, 01:39 AM
I would not think so as the amount of water and ammonia in the system are calculated to stop this happening.

Ian

Fridgeteach
01-09-2008, 06:18 PM
The volume (or weight) of ammonia you can absorb in water depends on the pressure. At normal room temperature and pressure water will absorb about 25% of ammonia. In an absorption refrigerator the pressure is about 2000 kpa and you cannot saturate the water.