PDA

View Full Version : oversized filter/drier



angryk
04-02-2003, 01:03 AM
What would be the effects of an oversized drier in a cap tube system?

herefishy
04-02-2003, 02:44 AM
my guess..............?

More refrigermerant!

That's all.

:D

Andy
04-02-2003, 10:06 PM
Hi,:)
also additional subcooling of the liquid, which would increase the capacity of the capillary, again leading to flood back.
This previous statement is again dependant on the placement of the drier, with driers facing vertically up causing the greatest increase in subcooling.
Regards. Andy

Prof Sporlan
05-02-2003, 03:17 AM
Extra note
========

Assuming the added liquid line volume inadvertanlty results in an increased charge.

The key here is a capillary tube system is a critically charged system. If the filter-drier acts like a receiver, then you can have some problems.

With a TEV, however, no problem... :)

angryk
06-02-2003, 01:28 AM
Thank you all for the info:cool: I don't know when but one day I will be able to answer someones question on the forum.:rolleyes: