Hello everybody,
This is my first message. I live in Estonia.
I have a question concerning pumping blended gases from rolldrums. They contain about 800kg of refrigerant. While I pump a liquid refrigerant, the proportion of blended gases remains accurate. But after pumping all the liquid gas there still remains quite much refrigerant as a gas. My question is: will the proportion of blended gases remain accurate when I suck the rolldrum empty with a recovery unit.
Hope my language is acceptable and you understand my problem.

cameron.e
08-11-2007, 02:58 PM
hi bud welcome to this great site,no it woulden't due to the mixture of the gases in the liquid so I would not really go with the vapor also, it would be fine if is it is being placed with the liquid in the same canester cheers

chillin out
08-11-2007, 05:56 PM
So long as you are putting the whole container in one system then there is no problem, When you are half way through a 800kg container then even the liquid you are drawing off is not 100% pure because it is constantly boiling off inside the container to fill the space where the liquid you draw off was.

Chillin:):)