PDA

View Full Version : Alco Expansion Valve


clum
06-11-2007, 06:23 PM
Hi everyone,

This is my first post, so be gentle!

I'm having trouble locating a replacement Alco expansion valve. The details I have from it are LMCHF4L. It appears to have a heater on the bulb which is fitted inside a pocket on a suction accumulator.

The refrigerant was R12 and is now R413a.

Any help or info would be much appreciated.

US Iceman
06-11-2007, 06:52 PM
I don't recognize the model number but the description you gave leads to me to believe you have a liquid level control valve. Sporlan also had something like this called a Level Master.

The heated bulb simply allowed the TXV to open, which allowed liquid refrigerant to flow through the valve and replenish the liquid in the accumulator.

When the liquid level in the accumulator reached the bulb, the bulb then cooled off, which forced the valve to close.

I tried to find the Sporlan document on their website, but it is going through a update right now, so I can't post a link for you to read about this.

Hope that helps in some small way.

PS. Welcome to the RE forums.;)

PaulZ
07-11-2007, 04:59 AM
Danfoss also make one it's a TEVA valve. It is basically a TEA 20,85 TX valve with a heater assisted power assembly and uses the same orifices ranging from 1 TR to 85 TR. These are generally used on NH3 but if you contact Danfoss they would be able to tell you if you can use it on R413a.

jose regueiro
08-11-2007, 08:04 PM
This is a "thermo valves for liquid injection", from ALCO Catalog 15.30 very old, Feb 1972. Search what they do.

jose regueiro
08-11-2007, 08:06 PM
The "heater" may be a coil from solenoids.

jose regueiro
11-11-2007, 04:14 PM
Big mistake, not "thermo valves for liquid injection", Look here XXX.frigodesign.ru/sale/sporlan/LiquidLevelControl_Sporlan.pdf[/url]

tech slave
22-11-2007, 11:07 PM
Hi the man to speak to is The Alco Tech/Sales Ian 07770586742

Regards

Tech Slave

PoodleHeadMikey
01-12-2007, 04:34 PM
Did you try calling ALCO ? I have always found them incredibly helpful, especially the engineering dept.

PHM
---------

jose regueiro
02-12-2007, 10:04 PM
It is SPORLAN, not ALCO. is a liquid level control valve

clum
03-12-2007, 06:42 PM
Thanks guys.

Jose, it is a SPORLAN valve and I found all the info on their website.