View Full Version : Daikin inverter compressor
Andy AC
23-10-2007, 11:02 PM
Hello guys,today I went out to a Dakin RXS60 inverter condenser with a duff outdoor pcb. Whilst I had it in bits, I noticed that the compressor has 4 wires going to it (4 terminals), whats that all about:confused: , I thought an inverter compressor was basically a 3 phase motor, so whats the 4th wire do?
Andy
cool#9
23-10-2007, 11:21 PM
Hello guys,today I went out to a Dakin RXS60 inverter condenser with a duff outdoor pcb. Whilst I had it in bits, I noticed that the compressor has 4 wires going to it (4 terminals), whats that all about:confused: , I thought an inverter compressor was basically a 3 phase motor, so whats the 4th wire do?
Andy
Hi Andy
If you mean the N terminal it's for the compressor rotor position (not a neutral wire).
This information is important for the pcb to anticipate the current through U, V, W terminal.
rgds
cool#9
Andy AC
23-10-2007, 11:39 PM
Thanks cool#9, that makes sense now
Andy