View Full Version : York Chillers



N.Lewis
23-10-2007, 02:20 PM
Hi guys, have an odd one here, have two york chillers on site, mod:ycva-55L-50B. Both chillers will shut down completly, have power to everything!! all pressures fine, but if i replace the inlet water sensor they imediatly start up again, being so old there is no fault code system, and it is imposs to get hold of york tech division, has anyone come across this prob or have any solutions??

Many Thanks...

themba
23-10-2007, 03:47 PM
make sure that all the sensors are in place and working correctly

Brian_UK
23-10-2007, 08:38 PM
What was the water temperature at shutdown?

paulwild
23-10-2007, 09:30 PM
try this contact number its for york/johnsson controls
they can e-mail you a manuel 01628246418

N.Lewis
25-10-2007, 04:43 PM
Hi guy's, had a day off hence late reply, to themba sensors are new and seated correctly, paul thanks for that number will contact them, and brian water temp when unit cutting out is approx 9.5 deg cels..
Just to clarify this has happened four times, and like i say popping a new sensor in seems to do the trick, but obviously cannot keep doing this!!

carlos_spain
17-11-2010, 07:36 PM
Hi,

Please, does anyone have the manual for York mod:ycva-55L-50B?